This occurs when you want a particular circuit to provide more electricity than its actual capacity.
Socket ring main keeps tripping.
An overloaded circuit is the most common reason for a circuit breaker tripping.
Discussion in electricians.
When too many appliances or light fixtures are operating at the same time the internal sensing mechanism in the circuit breaker heats up and the breaker trips usually by means of a spring.
It could just be a faulty mcb if you want to test it then swap it for the one same rating should be 32a that controls the upstairs ring main.
Hi my friends house has all his sockets on one ring main with spurs added through out the house all of a sudden the mcb triped also causing the 80rcd to trip aswel split load board so we dissconected every socket in the house and belled.
32amp mcb constantly tripping when no plug socket is in use.
So as zax47 says it s most likely a general fault on the ring main that s tripping and causing your main rcd to trip.
This will lead to the overheating of the circuit which puts all the electrical appliances.
Three reasons why circuit breaker keep tripping.
I have unplugged everything and it still tripped the rcd.
Electric keeps tripping our downstairs sockets.
I have also changed the sockets for double pole ones and it still trips the rcd.
It occurs when a circuit is attempting to draw a greater electrical load than it is intended to carry.
Changing the mcb didn t make any difference.
Is this now a problem with the wiring.
Call a pro to determine if a ground fault is why your circuit breaker keeps tripping.
In the world of wiring any time an abnormal surge of electricity occurs it s known as a fault or a.
Only the main circuit breaker trips not the individual breakers.
A circuit overload is one of the main reasons why circuit breakers trip constantly.